P = I X EP = watts, VA (Volt Amps)
I = amps
E = voltsHere we have a 100VA transformer. Manufacture spec 115Vac primary, 12Vac secondary.
Find the max available current, in amps, the secondary winding can safely deliver.
(Note: The max amp rating is determined by the wire gauge that was used to wind the secondary winding)100VA / 12Vac = 8.33 amps. So the gauge of wire used must be rated for at least 8.33 amps.
So how much current, amps, would the primary winding draw from the mains power if the secondary winding connected load is drawing 8.33 amps?
100VA / 115Vac (mains voltage) = 0.87 amps @ 115Vac. (Slightly higher due to losses)
(The wire gauge used to wind the primary winding must be rated to handle 0.87 amps minimum.If you had access to the transformer manufacture's data sheet for the transformer you would probably see Maximum Rated Primary current 0.87 amps at 115Vac. Maximum Rated Secondary current 8.33 amps at 12Vac
The manufacture supplied AC Line fuse is a 1.6 amps (slow blow) fuse. More than big enough to handle a continuous load of 0.87 amps of current the primary is drawing to supply 8.33 amps on the secondary needed for the connected load.
I am not sure why the 1.6 amp fuse is blowing with only a 3 amp connected load on the DC output of the power supply. One thing you might try is to install a temporary fuse in series with the DC connected load of say 4 or 5 amps. If the AC line 1.6 amp fuse still blows then there is something wrong with the power supply. If the fuse blows that is connected in series with the DC load then the problem is there.
By the why, what is the 3 amp connected load?
EDIT:
What is the AC mains voltage the power Supply is plugged into?Check the secondary AC winding voltage. What does it measure?
Measure with DC load connected.
Edits: 07/23/17 07/23/17
This post is made possible by the generous support of people like you and our sponsors:
Follow Ups
- RE: Zerozone 100VA PSU Fuse Issue - jea48 15:19:10 07/23/17 (21)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 16:58:00 07/23/17 (20)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 08:18:52 07/24/17 (18)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 10:23:29 07/24/17 (17)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 07:19:45 07/25/17 (16)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 15:29:49 07/25/17 (15)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 16:55:05 07/25/17 (14)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 17:23:35 07/25/17 (13)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 17:40:12 07/25/17 (12)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 15:13:03 07/27/17 (0)
- RE: Zerozone 100VA PSU Fuse Issue - Duster 19:31:07 07/25/17 (10)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 07:04:20 07/27/17 (9)
- Here is the NEC standard that looks applicable in this situation to me - Tweaker456 10:30:05 07/27/17 (8)
- I furnished that info already in an earlier post. - jea48 12:42:37 07/27/17 (7)
- UL code - Tweaker456 13:59:46 07/27/17 (2)
- RE: UL code - jea48 15:08:14 07/27/17 (1)
- RE: UL code - Tweaker456 16:03:42 07/27/17 (0)
- If this is correct there is no statement that it applies only to control tranies - Tweaker456 13:44:53 07/27/17 (1)
- RE: If this is correct there is no statement that it applies only to control tranies - jea48 15:01:53 07/27/17 (0)
- RE: I furnished that info already in an earlier post. - Tweaker456 13:30:50 07/27/17 (1)
- RE: I furnished that info already in an earlier post. - jea48 14:46:18 07/27/17 (0)
- RE: Zerozone 100VA PSU Fuse Issue - jea48 18:11:36 07/23/17 (0)