Home Tweakers' Asylum

Tweaks for systems, rooms and Do It Yourself (DIY) help. FAQ.

NEC 250.54 Auxiliary Grounding Electrode.

Quote.
One or more grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(c) or the resistance requirements of 250.53(A)(2) Exception, but the earth shall not be used as an effective ground fault current path as specified in 250.4(A)(5) and 250.4(B)(4).

Plain English you can install all the Aux grounding electrodes you want. Use any size grounding wire you want. Any type, any length earth grounding electrode you want. BUT it has to be tied to the existing branch circuit safety equipment grounding conductor that is connected to the ground bus in the electrical panel the branch circuit is fed from.
...the earth shall not be used as an effective ground fault current path as specified in 250.4(A)(%) and 250.4(B).

Does lightning love an Auxiliary Grounding Electrode? You bet!



Edits: 06/01/15 06/01/15 06/02/15 06/02/15

This post is made possible by the generous support of people like you and our sponsors:
  Kimber Kable  


Follow Ups Full Thread
Follow Ups

FAQ

Post a Message!

Forgot Password?
Moniker (Username):
Password (Optional):
  Remember my Moniker & Password  (What's this?)    Eat Me
E-Mail (Optional):
Subject:
Message:   (Posts are subject to Content Rules)
Optional Link URL:
Optional Link Title:
Optional Image URL:
Upload Image:
E-mail Replies:  Automagically notify you when someone responds.